(EDIT: sorry, yes, I meant 120V outlet)
(EDIT: sorry, yes, I meant 120V outlet)
One good test that I saw somewhere that I do on new outlets I am charging on, is leave the car charging for ~30 minutes and then quickly unplug the charger from the wall. Touch the prongs to your hands. If they are very warm or hot, you are likely over-drawing that outlet and need to ramp down your amperage draw (or better yet, find a new outlet).
This article focuses on outlets but the wiring is just as (or more) important and outlets can very easily be installed with under-code wiring.
The issue in the circuit ampacity for standard residential outlets - typically, a 120v 15 amp plug will be wired in 14 gauge NM-B wire (romex), which already de-rates the maximum temperature the wire jacketing is allowed to reach over higher ampacity wire (THHN) which is typically run in conduit. For a given wire gauge, THHN has more ampacity and the jacket is rated to a higher temperature.
for a 20amp 120v circuit (not common unless you install intentionally for that purpose) you need 12 gauge wire.
But, as mentioned in the article, continuous loads need to be up-sized because of temperature, and even standard outlets for the correct ampacity circuit don't often anticipate 100% duty cycle.
BUT, the real question is for your trickle charger, how many amps does it draw? if it tries to draw 12 amps on a 15amp circuit, everything is fine. If it tries to draw 15-20 amps on a 15 amp circuit, there is some danger. Many breakers (esp older ones) will not actually pop if the amp demand ramps up slowly.
Ampacity Charts: https://www.cerrowire.com/products/resources/tables-calculat...
Source: I've wired a LOT of power tools with big loads, but I am not an electrician. Take this advise as indicative and decide whether it warrants you contacting an electrician to validate your situation.